Carrier 48GS package unit Carbon Monoxide issue!

17K views 51 replies 11 participants last post by  albrantley  
#1 ·
I installed a new heat exchanger, inducer draft motor assembly, & the back plate for the draft motor today and after getting it done I started it up and everything came on fine. The 2 shot burners where burning blue and the outlet pressure was running around 3.2 to 3.3. However, after I was gone for about 2 hours the H/O called and said that there CO monitor was going off. When I got there I started it up and the gas valve didn't want to open up but after several attempts it finally did. The flames look great but i am getting a strong smell like a rich mixture but there is no adjustments that i can see on the burners for the air. i am getting an elevated reading in the house but i took the right side panel back off to check everything and it looks sealed up with no way of sucking the exhaust back into the system. I am stumped and can't think clearly at this point. I have never had this type of issue before after installing one before. The only thing I know of right now that doesn't seem right is the rich smell I am getting out of the flue and that is it!!!. Can someone help. Could a faulty gas valve cause this to happen?
 
#51 ·
Ran a call the other day identical to this thread. Odor was strong with CO levels around 15ppm. Heat exchanger was ok and draft motor rotating the right way. No economizer package to allow extra infiltration. Long story short gas valve inlet 7.9 outlet 6.0. Natural gas. Replace valve all good. The previous response to my question sunk in much more after this call

Sent from my SGH-T999 using Tapatalk 2
 
#40 ·
I would go back over that HX install again with a fine tooth comb.

I know the burners have a particular way they lay on each other that might be another thing to check, along with alignment in the opening.

Gravity might have already sent it too you, but I'll email you a pdf of how they go together.
 
Save
#37 ·
If you think the CO is coming from this unit, it really needs to have a combustion analysis done, because it is producing way too much CO.


Here is an explanation by Jim Davis about how much CO the unit has to produce, to get any CO inside the structure.


A 100,000 btu furnace uses 25 cfm of air for complete combustion. Furnace blower in heating move 1300 cfm on draft induced and 1500 cfm on condensing.

If you mixed 100% of the flue gasses with 1500 cfm how much CO would you have to be making to get a reading of 10ppm?

25cfm is .016% of the mixture, therefore the furnace would have to be making over 600ppm which exceeds the 400ppm "air free" they are allowed.

The furnace would have to be red-tagged without a hole or crack.

That is dumping 100% of the flue gasses into the airstream. A crack may under certain conditions may leak say 2% of the 25 cfm or say .5 cfm. .5 cfm is .003% of 1500ppm.

So to read 10ppm of CO in the airstream, the furnace would have to be making over 3000ppm of CO.

Even without the blower running the volume of air in the plenum versus the volume of air from a leak would be still be quite diluted
.


Bottom line: To get measureable CO in a space an appliance,or vehicle, has to be making seriously high levels of CO, or it has to have been made over long periods of run time.
 
Save
#36 ·
how would the furnace flue gases get into the home?

you are allowed by ANSI standards to have 400ppm CO airfree or "CO(0)" in the exhaust. I was trained CO under 100ppm undiluted, which I've been able to achieve on every appliance.

so if your under 100ppm CO in the flue then your good. Now you need to figure out how its getting into the home.

opened windows? blower door has a gap? heat exchanger not sealed around air gaps? have car started in garage? they cleaned the electric over and didn't ventilate the home?
 
#30 ·
i sent you 2 pdfs. one shows the correct way to mount the burners. maybe they got flipped. the other one shows the flue baffle.

i'm thinking flame impingement of misaligned burners or gas needs to go up or down.

you said originally the nipples arent even. the slightest offset could mess everything up. i would make sure 100% the burners are lined up perfect.

also might need the flue baffle with such a small heat exchanger
 
#22 ·
i noticed that both part #'s have a 500 in it but the part #'s i have for two of the parts have 400 in them. Such as the inducer fan assembly is a 48gs400649 and the flue box collar is a 48gs400108. I do not know if this means anything?
 