have a carrier 100 ton 30gt air cooled chiller. Another one of the techs was on the machine and determined that the B circuit EXV was bad. I returned to install the EXV. Replaced and pulled down to 400 microns, also replaced both saturated suction thermistor and suction gas thermistor.Started chiller and let run for 10 minutes, pressures 200/40 and slugging both B circuit compressors with liquid. As it turns out the same problem the first tech had. Unit it maintaining 27 degrees SH but shuts EXV all the way down to do it. Called factory and they suggested to recover charge and weigh in factory charge. Returned and recovered also drained 3 gallons of oil out of cooler, weighed in 105 lbs. of R-22 and started chiller let run and found pressures doing the same thing. I know the ciller does not care what the pressure are it will shoot to maintain 30 degrees SH. I have double and triple checked all my sensors and EXV and cable I am at a loss as to why the EXV is closing and still slugging liquid, sounds like a chainsaw on start-up