Houston, Texas
Pioneer 12k BTU Inverter+ WYS series installed in garage workshop.
Not a pre-charged line set. Install instructions clearly called for evacuating the line set and adding refrigerant. Techs didn't bother reading those... bottom line, they did not pull a vacuum on the system. They hooked up the piping, released the factory charge and fired it up - no vacuum pulled, no charge added. When I asked them about it, I got something along the lines of "these units don't require a vacuum to be pulled... they are high tech" They said the delta T was good and called it a day. They recorded the system parameters on the warranty registration:
142 psi
97 ambient
return air 87F
supply air 64.8
this was at initial startup, garage was at 87F.
I used to work in the plumbing and electrical trade so I had already mounted the equipment, routed the line sets and completed all electrical... this was a pure HVAC install scope that I knew I needed a professional for.
Got a quote from a local shop to connect the refrigerant lines, evacuate the system, and add 0.16oz of R410a per foot of line beyond the 16' standard charge. This one had a 33' lineset. (This shop had good recommendations on one of those phone apps.) The quote was reasonable for the amount of time it would take to pull the vacuum, pressure test etc... I was guessing 45 minutes to an hour of time req'd. They were done in about 15 minutes.
System fired up and is keeping the garage workshop at a nice 75 degrees.
From reading on your site forums, it looks like the install was botched and I'm looking at a reduced system life. Questions for the pros:
a) Based on above, was the install "deficient"?
b) How bad is it?
c) Any advice ?
Pioneer 12k BTU Inverter+ WYS series installed in garage workshop.
Not a pre-charged line set. Install instructions clearly called for evacuating the line set and adding refrigerant. Techs didn't bother reading those... bottom line, they did not pull a vacuum on the system. They hooked up the piping, released the factory charge and fired it up - no vacuum pulled, no charge added. When I asked them about it, I got something along the lines of "these units don't require a vacuum to be pulled... they are high tech" They said the delta T was good and called it a day. They recorded the system parameters on the warranty registration:
142 psi
97 ambient
return air 87F
supply air 64.8
this was at initial startup, garage was at 87F.
I used to work in the plumbing and electrical trade so I had already mounted the equipment, routed the line sets and completed all electrical... this was a pure HVAC install scope that I knew I needed a professional for.
Got a quote from a local shop to connect the refrigerant lines, evacuate the system, and add 0.16oz of R410a per foot of line beyond the 16' standard charge. This one had a 33' lineset. (This shop had good recommendations on one of those phone apps.) The quote was reasonable for the amount of time it would take to pull the vacuum, pressure test etc... I was guessing 45 minutes to an hour of time req'd. They were done in about 15 minutes.
System fired up and is keeping the garage workshop at a nice 75 degrees.
From reading on your site forums, it looks like the install was botched and I'm looking at a reduced system life. Questions for the pros:
a) Based on above, was the install "deficient"?
b) How bad is it?
c) Any advice ?