Are there problems? Yes. Pump orientation is one. But guess what guys. That piping is not responsible for the air getting in the system. There are thousands of systems that pump into the boiler and into scoops. Guess what? They work. Is it ideal? No, but they still work. Pipe it like chuck shows and life is usually good.

Check the expansion tank first. Then, I would offer to repipe the boiler room, no charge. Do it like chuck shows, add lots of isolation valves. Isoflanges on the pump, valves on both sides of the zone valves, a valve then a drain valve on the expansion tank, Supply and return on the boiler.

Get rid of the di electrics on the pump.

Make it look nice and make it easy to service.

I'll bet he recommends you to other boiler owners.
 