I had my first Blower door test and Combustion analysis test done today as part of a NJ state sponsored energy Audit. I have nothing but praise for the BPI accredited Pro that did the work (and it is not because he offered me a job
...twice
, Thanks HVAC-Talk for my education in this area. Best $125 I ever spent for 4 solid hours of work. If it was not state sponsored it would cost much more...If you live in NJ I reccomend you take advantage of this opportunity.
Ok, now lets get dow to business. I will start with the combustion analysis since I have participated in some very intense and excellent threads on the subject of whether 1st or 2nd stage is more efficient.
The tech used a Bacharach combustion analyzer and checked both 1st and 2nd stage heating operation. Oh before I forget, I have a 100k BTU Trane XV95 furnace and a 4 ton XL15i AC with matched 5 ton ADP coil.
Here are the numbers for 1st stage:
Stack temp = 90
O2 = 8.4
CO2= 7.1
ambient temp = 72
CO= 5 ppm
Efficiency = 98.3
Here are the stage 2 numbers
Stack temp = 105
O2 = 8.3
CO2 = 7.2
ambient = 74
CO= 4 ppm
efficiency = 95.0
I know the O2 numbers is not as low as 6.0 like the great Jim Davis likes to shoot for but what do you think?
I have to run for about 45 minutes will be back to post more data.
Key1
Stack temp = 90
O2 = 8.4
CO2= 7.1
ambient temp = 72
CO= 5 ppm
Efficiency = 98.3
Stack temp = 105
O2 = 8.3
CO2 = 7.2
ambient = 74
CO= 4 ppm
efficiency = 95.0
Key1