Looks like a Rube Goldberg :D

Piping is wrong, it is a hack, it should either run in series then go to the receiver last, or in parallel then go to the receiver last, cant see a point in further cooling of liquid refrigerant? If I were doing it, it would be in series, but I have never done that yet?
Ditto that. eek 2eek 2eek 2

Wash your hands, quote a proper installation with a properly sized unit.

That is a disaster waiting to happen to you.

Earlier, I was using Blackberry. I thought that was what I saw, but needed a better picture to be certain.
 
I've done a little thinking about this one.

While it is 'hacked up' I think that it can be fixed.

Viewed from an operational standpoint, I have seen heatcraft condensing units piped using the same sequence (coil-receiver-coil-txv)

It will take some fiddling, but I would start with a clear glass and new driers. Use sporlan 90-30-1 document to calculate charge needed to flood condenser in low ambients.

Work from there on SH. Trying without a solid column of liquid is a waste of your time. Maybe burn in a sightglass and pressure tap at the coil while you are there.

Have fun, you will learn a lot on this one.
 