I had an Aprilaire 500 humidifier professionally installed. The humidifier appears to be installed correctly and appears to operate properly when triggered, but I can't seem to keep the thing running long enough to make any impact on the humidity level in the house. The humidistat installed on the return duct is reading 45%+ RH at which point it turns the humidifier off. The actual humidity level in all areas of the house is reading 20-23% on another portable humidity monitor. The outdoor air temperature sensor is properly connected to the humidistat and is on the east side of the house.
Any thoughts on why there might be such a large variance between the humidistat's RH calculation and the actual humidity levels in the house? Based on what I have read online and in the manual, the humidifier control is doing its job turning the humidifier off when the humidistat reads 45% (based on the settings I have dialed up). I just don't know why it's reading so high when the house is as dry as it is. I have even tried placing the portable humidity monitor directly outside the grill of the main return duct. There is still a 25% variance in readings between that monitor and the RH monitor on the humidistat.
Other factors that may or may not make a difference: outside air temperature is approx. 27 degrees F, AHU/humidifier/furnace is installed (hanging) in an uninsulated garage (approx 38 F currently), indoor air temperature is approx. 68 F, humidistat is installed in the center of a 6 foot, uninsulated return duct.
Thanks folks. Any thoughts you could provide will be helpful.
Any thoughts on why there might be such a large variance between the humidistat's RH calculation and the actual humidity levels in the house? Based on what I have read online and in the manual, the humidifier control is doing its job turning the humidifier off when the humidistat reads 45% (based on the settings I have dialed up). I just don't know why it's reading so high when the house is as dry as it is. I have even tried placing the portable humidity monitor directly outside the grill of the main return duct. There is still a 25% variance in readings between that monitor and the RH monitor on the humidistat.
Other factors that may or may not make a difference: outside air temperature is approx. 27 degrees F, AHU/humidifier/furnace is installed (hanging) in an uninsulated garage (approx 38 F currently), indoor air temperature is approx. 68 F, humidistat is installed in the center of a 6 foot, uninsulated return duct.
Thanks folks. Any thoughts you could provide will be helpful.