8 x 8 x 21' box, panels in poor condition, extremely heavy traffic, door propped open frequently. Original setup 2hp / 16 btu evap, we went back with 3hp 26k btu evap. Condensing unit is underneath a storage shelf but shelf it is about 1ft away from back wall so a little bit of fresh air can get in. They did not want us to relocate unit. Ran new lineset 1-1/8 x 1/2 ACR. Turned out nice, I was pushing to go with a 3.5 or 4hp due to 112°f air entering condenser but it got political and bosses went with the 3hp. Worked out ok although runs a fairly high evap SST which I don't like. I'm very proud of my trainee who did an excellent job piping in a brand new drain line and tying in the electrical.
Sent from my SAMSUNG-SM-G890A using Tapatalk