I've had this issue for years now and I need some help or guidance.
My A/C does blow cold air but will not cool down the house less than 78. It's very hard to cool below 80. A/C often stops at 80 when it was set for 78 or lower and restarts. I set thermostat to 82 till 7:30 PM and 78 for the rest of the night
From supply to return, the temp difference is mostly 16-20 degree on any conditions. Two techs I called said my unit is working just fine since I do have the good temp difference and air flow was good. ( nobody checked with gauge though) . One said it's just undersized. However, I didn't have this issue before I replaced this unit. It's been a problem since the installation of the unit but I have been believing that the original HVAC company said everything is per the spec and normal. The weather wasn't very hot for years like this year.
The outside unit is just two years old, Goodman 13 seer. 4 ton, GSX130481. I saw other post with the similar issue and did some reading. (11:45PM).
When outside temp is 94 degree with 45% humidity, condenser discharge temp is 108.. Temp split is 14
Indoor humidity is 50% with 80 return and 60 supply. I have two returns with 12 vents
The unit ran from 7PM to 12 PM to drop temp from 82-80.
I want to call another company not hoping to hear I don't have any issue..but the unit is running almost constantly and still not cooling down the house. This is for 2nd floor of about 1800sq. It was 102 ish today. I added extra insulation, vent and radiant barrier in the attic. I had very cool summer before regardless of outside temperature.
any ideas?
My A/C does blow cold air but will not cool down the house less than 78. It's very hard to cool below 80. A/C often stops at 80 when it was set for 78 or lower and restarts. I set thermostat to 82 till 7:30 PM and 78 for the rest of the night
From supply to return, the temp difference is mostly 16-20 degree on any conditions. Two techs I called said my unit is working just fine since I do have the good temp difference and air flow was good. ( nobody checked with gauge though) . One said it's just undersized. However, I didn't have this issue before I replaced this unit. It's been a problem since the installation of the unit but I have been believing that the original HVAC company said everything is per the spec and normal. The weather wasn't very hot for years like this year.
The outside unit is just two years old, Goodman 13 seer. 4 ton, GSX130481. I saw other post with the similar issue and did some reading. (11:45PM).
When outside temp is 94 degree with 45% humidity, condenser discharge temp is 108.. Temp split is 14
Indoor humidity is 50% with 80 return and 60 supply. I have two returns with 12 vents
The unit ran from 7PM to 12 PM to drop temp from 82-80.
I want to call another company not hoping to hear I don't have any issue..but the unit is running almost constantly and still not cooling down the house. This is for 2nd floor of about 1800sq. It was 102 ish today. I added extra insulation, vent and radiant barrier in the attic. I had very cool summer before regardless of outside temperature.
any ideas?