Hey guys,

I come across 4-20 mA control systems and sometimes have to spec parts and modifications. So...

Some devices generate a carrier DC voltage, about 10 to 30 volts, and some don't. I figure I need one device generating the voltage and the others not, in a loop.

My problem is that some suppliers don't clearly state whether the carrier voltage is supplied by them or not.

What is the vocabulary or 'phraseology' (ask Paulin), that I should use when clarifying these devices and the specs needed?

Thanks for the lesson in controls-tech-talk.

And while you're at it, throw in your 2 cents worth on dry and wet contacts. I've been curious to know.

Dave
 
Source = sends power to the loop
Sink = draws power from the loop

Typically if the sensor is 4 wire, 24 power and 2 wires for the 4-20ma it almost always sources power to the loop. If it's a two wire end device, its typically sinks power from the loop.
 
When in doubt....smoke it out. If you're really the responsible one, you're in trouble. You need to get yourself some product literature, start doing some serious reading, set yourself up a test bench with the product you're working with, and learn this basic stuff. This is another example why working in the field and getting your hands dirty is so very very important. Over the years I've worked with several folks who thought controls was nothing more than the ability to sit in front of a computer and push buttons. Most of them are no longer in the business.
Wet.....often a triac controller binary output. (often 1 binary output wire terminal with the powered coil common back to the controller power common) Don't short it, sometimes they're tender. Dry.....a controller binary output often used to switch an external power source just like a light switch. (often a form c style controller binary output with 3 terminals nc c no). 4-20 analog devices are usually 2 wire or three wire. A 2 wire normally accepts controller power and returns it's signal back to an analog input. A 3 wire usually takes controller power, and power common, and returns it's signal back to the analog input. There are many variations with respect to voltages and ranges. Always consult your controller data, follow the device installation instructions, and set up your controller properly. Wire these suckers wrong, and depending on the product, they'll either not work correctly or smoke the device, the controller, or both. If I had a choice, I prefer to not use 4-20ma devices. 0-10v, or even 0-20ma devices are much easier to work with. Let's see? what's 50% on a 4-20? Damn...I got to lift another wire to read the stupid thing...........what happens if I add a 500ohm resistor?
 
Hey guys,

I come across 4-20 mA control systems and sometimes have to spec parts and modifications. So...

Some devices generate a carrier DC voltage, about 10 to 30 volts, and some don't. I figure I need one device generating the voltage and the others not, in a loop.

My problem is that some suppliers don't clearly state whether the carrier voltage is supplied by them or not.

What is the vocabulary or 'phraseology' (ask Paulin), that I should use when clarifying these devices and the specs needed?

Thanks for the lesson in controls-tech-talk.

And while you're at it, throw in your 2 cents worth on dry and wet contacts. I've been curious to know.

Dave
I've no idea what you mean by using the term "carrier" here.

4-20 ma signal generating devices have been around a long time. As have 0-20 ma devices.

In the industrial/process control and instrumentation worlds 4-20 ma signaling devices are seen to have a couple advantages over the 0-20 ma devices.

First, if the instrument, sensor or whatever had a low enough power requirement (the power needed to operate the sensor's internal electronic circuitry), it needed no additional power supply plus associated wiring. i.e. Typically you just needed two wires to connect to it. One providing 24 volts DC. The other being the output signal. The instrument drew its own internal power needs from that 24 volt supply, with a maximum draw of less than 4 ma. The "signal" is the modulated current flowing through the loop. With 4 ma being the "low signal" and 20 ma being the "high signal". The sensor modulated the current flow at some point between those two values to represent a proportional value of the MV (measured variable). Such as pressure, temperature, or whatever.

It was quickly realized that this had an additional advantage. A second reason to prefer such method. And that is if you monitored the signal (current), and its value went significantly below 4 ma or above 20 ma then you probably had a fault condition. A failure of some kind. Wires were cut, sensor was playing dead cockroach, or whatever.

In fact the line of controllers we use most often recognize this and will flag a 4-20 milliamp input as "unreliable" if the input goes below 3.5 ma or above 22 ma.

If the sensor/instrument can get by with needing less than 4 ma for its own internal circuitry needs, its most often "loop powered". Meaning that it draws its power from the current loop. The loop formed by the current flowing from a 24 volt DC source (external from the sensor), to the sensor, out of the sensor, back to the input of the controller, back to the common of the power source.

For instance, all two wire ma sensors are "loop powered". They are consuming some of that current below the 4 ma level.

Some 4-20 ma signaling instruments/sensors require more than 4 ma to power their internal circuitry. For instance, CO2 sensors of every make I've seen so far used in the BAS industry.

In such cases, those will be 3 or 4 wire devices. The additional wires are needed to provide adequate power levels for the sensor circuitry. Typically a 12 or 24 volt AC or DC power supply on two wires. Then internal circuitry within the sensor powers and modulates an isolated 4-20 ma signal on the remaining wire(s).

Typically a device manufacturer provides cutsheets that indicate whether the device is "loop powered", needing only two wires, or whether it needs a separate power supply (2 wires) plus signal carrying wire(s).

For instance, a particular CO2 sensor we commonly use requires (consumes) about 70 ma for its own internal circuitry needs. Obviously, it can not be "loop powered".

As to wet and dry contacts.

Typically "dry contacts" refers to the opening and closing of contacts that have no voltage or current applied to them by the equipment having said "dry contacts". They're "dry". You sense the opening or closing by whatever method your equipment requires, can handle. Typically by placing a potential (voltage) on one side and checking to see if there is a voltage/current appearing on the other.

"Wet contacts" usually mean that the equipment providing such is presenting a voltage on the two wires to indicate closure, or an absence of voltage to indicate open contacts. You'd sense contacts "closed" by reading/detecting a voltage on an input, or by having said voltage pull in a relay (of proper coil voltage) and then reading the condition of that relay's dry contacts. Or whatever.

For instance, recently I needed to pick up an input from a machine that would indicate a fault had occurred and its controls were locked out. All that was available inside the device's internal circuitry was a "wet contact". Meant to power an alarm bell or light. No voltage, everything was fine. 120 volts AC present on the two wires mean a fault condition. I just put in a little 120 VAC relay, coil connected to the two wires. And connected my wires for my controller input to dry contacts of said relay.
 
Osiyo is completely correct on the current-based sensor discussion above.

But to drive it home in another way, here's what you need to remember:

A 4-20ma signal (a 0-20mA signal wold work the same way) specifies the amount of current that it will pump out based on the sensor's present reading. There isn't a "carrier voltage as you have suggested."

The actual voltage on the wire is driven by the equation V=IR. Since I is the current and the resistance of the input of the controller can be known, you can determine the voltage that would be on the line if you sensed it with a voltmeter.

Let's say that the input on the controller has an impedance of 100 ohms. If you fed a 20ma signal into it, you'd end up with the following:
V = IR = .020 * 100 = 2 volts.

If you had the same 20ma signal feeding into an input that had an impedance of 632 ohms (for whatever reason) the voltage at that input would be:
V = IR = 0.20 * 632 = 12.64 volts.

Of course the controller itself would see the same current (20ma in these two cases) regardless of the voltage that is generated due to the input impedance that the mfg chose to add to the input.

So you see, the concept of a "carrier voltage" is an incorrect notion.
 
I don't know a good term for it either but i understand your issue. We had to take 4-20mA outputs from a Sieman's pool chemistry controller so they could see pH, temp, etc. on the BMS.

Since the output voltage from the Sieman's boards was around 87-90vdc, we could not run that straight into our controller and had to use isolation modules which are not cheap (but they come in handy for situations like this).
 
You have to determine which device is powering the loop. It's not always stated or obvious. Some stuff will have like a 15VDC power supply driving it. Some controllers can only power the input side and not the output. It's all every which way in reality.

Go get a 5W or more skookum 500 ohm resistor and play around. You will see 10 VDC across the resistor at 20 mA. Ohm's Law, my friend.

We all started at the same place in this field and should never be so proud as to forget that fact.
 