I was looking around on ebay and saw a wshp that was 265 volt the seller said it would work with 240 ,265, and 277 not too experienced with 265 I have only worked on a data air unit 1 time someone enlighten me please? Sorry for the run on sentence.
 
#4 ·
I installed a leibert ahu that was 240 the power supply voltage was 277 .Had to use a transformer to buck the power down to 240 to make it work. This leaves me more confused.
 
#5 ·
The boost/buck transformer only carries a small percentage of the actual load.In this case 277-240 = 37 volts and the same percentage of amps. You would use a 32 volt to buck it down to 245 volts.
You take a 12/24 x120/240 or 16/32 x 120/240 transformer and add or subtract 12,16,24,32 volts from the original voltage. Square D and several other sites have charts to make size selection simpler.
 
#8 ·
Sometimes the 277V version of a fan coil is a 240 volt one shipped with a transformer.

I never wired one of those up myself wolf, what do you do about the ground wire?

Is is a grounding electrode conductor after the buck and boost?
 
#9 ·
The buck/boost transformer does not have a grounded component.
Use the ground as you normally would.

For 277 to 240 volts, invert the drawing.

(attached picture thanks to the excellent ECN site)
 
#10 ·
One phase

265 Volt is one phase of 460 Volts. Very popular in enviromentally friendly buildings. You cannot use a 265 volt unit on a 240 supply. You will burn up transformers and contactor coils like crazy.
 
#14 ·
277 is the common voltage for building lighting, derived from 460-480 as described above. For a 240 volt supply, do use a transformer.

I'm still wondering what a "wshp" might be. :confused:
 