Have a 25 ton intellipak, lost a comp shortly after a large refrigerant leak in July. Had to replace one condenser coil and compressor. Ran well until October the lost the same compressor again. Locked up, busted scroll. Replaced, as well as LLD and contactor. Recharged with factory charge weight 55#. All vitals looked good. Ran a a month and dropped it again, rinse and repeat. Checked everything on tracer SC, have VAV mins @ total of 4100 CFM, 20% outdoor air, medical facility. Did find low ambient fan actuator with stripped gears and failing, superheat at 10* both comps running, 5* SH with a single comp running. Supply static 1.6”. Noticed every few cycles the compressors would start hard with liquid flooding for a few seconds then smooth out. We suspected TXV sticking. CCH are working. Replaced TXV and another compressor, this time compressor 1 the 10t on the tandem, that’s the first time it’s been changed. Even after new txv still have flooded starts, adjusted txv to maintain superheat around 16-20* depending on one or both comps running. I have no idea what’s causing the flooded starts! The building had a low load, single duct VAVs with HW reheat. I know the return is a little undersized, but it’s been running without hick up for 10 years.
Suction restrictor is the correct size and is in correct compressor.
These compressor failures are never electrical, it’s always lock rotor, one was bad enough to have dents poking out of compressor shell.
Suction restrictor is the correct size and is in correct compressor.
These compressor failures are never electrical, it’s always lock rotor, one was bad enough to have dents poking out of compressor shell.