Ok I know there is a lot of you that are going to say "just put in a separate unit and be done with it!" or "why mess with it?" Well, where is the fun in that! I have an existing 3 ton condensing unit and furnace. The plan is to build an out building that will need some A/c in it. I am going "T" into the line set at the CU. I figured I will put liquid line solenoids and check valves at the CU for both coils. The furnace already has a TXV. The outbuilding will also. Here is another thing; the coil in the out building is going to be 1.5 ton.
OK, the logic is going to be when the 3 ton furnace calls for cooling the solenoid will open on the 3 ton furnace, the 1.5 ton solenoid will be closed. When the 1.5 ton calls for cooling with the 3 ton, I will modulate the CFM across the 3 ton coil to an effective 1.5 tons. I will keep priority to the 3 ton furnace because it’s the house where most everyone is. So in saying that if the furnace cannot keep the house within 1 or 2 degrees I will turn off the 1.5 ton, closing the solenoid and close the air bypass at the 3 ton. Now what if the 1.5 ton needs cooling and the 3 ton doesn't? Hot gas by-pass? or... I dunno. I don't want to change the CU to a two speed or anything. The CU and the furnace is just a couple of years old. I just want to add the 1.5 onto this rig and see it work! I will have a DDC controller and be able to have pressure inputs and so on so it’s not going to be a "duct tape and relay" job.
So here is what I have so far:
1. Rheem 13 SEER furnace and condensing unit.
2. VLC-853 Alerton controller
3. VLC-651R Alerton controller
So what do you think?
OK, the logic is going to be when the 3 ton furnace calls for cooling the solenoid will open on the 3 ton furnace, the 1.5 ton solenoid will be closed. When the 1.5 ton calls for cooling with the 3 ton, I will modulate the CFM across the 3 ton coil to an effective 1.5 tons. I will keep priority to the 3 ton furnace because it’s the house where most everyone is. So in saying that if the furnace cannot keep the house within 1 or 2 degrees I will turn off the 1.5 ton, closing the solenoid and close the air bypass at the 3 ton. Now what if the 1.5 ton needs cooling and the 3 ton doesn't? Hot gas by-pass? or... I dunno. I don't want to change the CU to a two speed or anything. The CU and the furnace is just a couple of years old. I just want to add the 1.5 onto this rig and see it work! I will have a DDC controller and be able to have pressure inputs and so on so it’s not going to be a "duct tape and relay" job.
So here is what I have so far:
1. Rheem 13 SEER furnace and condensing unit.
2. VLC-853 Alerton controller
3. VLC-651R Alerton controller
So what do you think?