I changed two compressors this week both at the same site.Same type condensing units,low temp. ..R-404A...walk in freezers...pump down systems..rooftop condensing units..lab.building..maintaining -15 degrees in box.Compressor # AVA2490ZXT. Units have cond. fan cyclers only for head press. control.Both replacement compressors came without crankcase heaters and the originals did not have them either.The units do not have suction accumulators.Both replacement compressors had wells for self regulating type heaters and I thought it would be good refrigeration practice to apply heaters to the compressors.The supplier did not have self regulating type so I used 90 watt 230 volt band type. My delema came at the point of wiring them in.I've seen it done both ways .....across the line,hot all the time...and on normaly closed aux. contacts...hot only when the compressor is off.I chose to wire it hot all the tme.Did I make the right choice?I changed contactors,liq. line drier,installed suction drier,deep vac.,all the proper stuff,start up and check out went well,perfect super heat, temps. pressures,the whole nine,tested pump down, defrost,cycle controls and ,every thing checked out.One faild pump was grounded and the other had bad valves.I'm wondering if possibly the failures were a result of not having heaters in the first place.I know it"s a stretch? Any way Im more concerned about the heater wiring.Any thoughts??????,