I have searched the threads for information about the transducers that may be helpful, but was unable to locate information pertaining to my situation.
This YCAS system has had its share of problems but not as bad as others I have read about. ( I better knock on wood!) Winding sensor corrosion has been a big problem along with condenser motor bearings.
M/N YCAS0140EC17YGADBC
Compressor DXS24LASB17 Part Number 364-49095-212
The problem is with the discharge pressure transducer Part Number 025-29139-001 or Danfoss AKS32R 060G2154 0-400 PSIS 5VDC signal.
The number 1 circuit compressor seems to be causing a harmonic vibration that is damaging this transducer within a 1 day period. The sensor will fail to 399 PSI and lock out the compressor in the micro panel, as it should. If you lightly tap on the sensor it will read erratic until it goes to full failure. Removing the sensor from the circuit and plug in with no pressure on it it will read 399 Psi.
Checked wiring harness by isolating bot end and ohm test. Also, checked 5V DC voltage input to sensor and signal out put while in operation with a known good transducer with system running. A new known transducer will read good for a while then start to fail bu reading erratic pressures from actual pressures to 4 to 50 psi.
I found by chance if you wrap a rag tightly around the transducer, the rag will dampen the compressor harmonics enough the allow the transducer to read correctly.
What am I missing? Could there be a muffler or baffle plate problem?
Any thoughts out there.
I will return soon and check to make sure the compressor shipping mounting bolts were removed at startup 4 years ago.