We have a problem with the screw compressor on the chiller RTWB212. Low oil temperature on the return to the compressor (30-35 degrees Celsius) and generally low cooling capacity. The current load goes up, but the compressor is not actually loaded. We assume that the compressor has insufficient oil flow in the oil system. The oil and filter on this chiller was changed 2 years ago. Checked the correct assembly of all things (solenoid valves, all gaskets, screens). The pressure on the shredder on the oil filter is 0.5 bar below the discharge pressure. Oil pressure is low. The tube at the outlet of the oil separator is already almost cold, and the discharge temperature after the compressor is 60 degrees Celsius.
We have a suspicion that the oil valve, which is after the filter, is not working properly, but we are not sure...
What can be your recommendations and advice on our problem?
Thank you!
Thank you!