Is anyone having any issues with Trane Compressors making a loud noise before going into thermal overload. I’ve ran three calls on new equipment we’ve installed doing this. Any help is really appreciated.
I don’t think it like power blip. I noticed it a few times when I check the SS2 float switch for water while the system running. I was not careful and cut the outdoor off momentarily. Immediately I heard the compressor making loud noise and going into overload.Is anyone having any issues with Trane Compressors making a loud noise before going into thermal overload. I’ve ran three calls on new equipment we’ve installed doing this. Any help is really appreciated.
I am not trying to be rude but his is a long post with very little information in it to help with diagnosing your problem. The only real data is 186/260 for pressures the one time you saw it happen which are not normal pressures for a properly operating system.I’ve only seen the problem occur once on site.
The other two we’ve just been aware of due to customers taking videos for us.
That we are aware of, it has happened to three of our Trane Systems. One 14 SEER 5 Ton, and two 16 SEER 3 and 2.5 tons.
These are scroll compressors.
When we arrive to check the systems
Refrigerant charge is perfect
Superheat and subcool values are good.
Amp draw checks out.
On our first customer we replaced the compressor, no luck.
We went back and replaced the TXV, no luck.
We went back and flushed the entire system with r11, no luck.
We went back and replaced the entire coil with a different brand using a piston, no luck.
The system will cool just fine for a few days then it will make that noise and go into thermal overload. Once it cools back down it works just fine for a few days.
When I saw the fault happen in person the refrigerant pressures were
Suction 186 liquid 260
The thing that has us stumped is that our first two customers it happened to have not called us back in about a week because it hasn’t done it again.
I’m looking to see if we are the only ones having issues with this on Trane Products.
I do have a video of the systems making that “clicking” noise but I don’t think I’m allowed to post it since I’m new to the forum
~1992 Lennox had a problem with ss antirecycle boards. Contactor chatter could cause the compressor to run backwards if pressure had not equalized before starting. Compressors would run until tripping discharge t’stat. I would test by dragging the t’stat run wire across the terminal to make sure it would lock out on antirecycle.I just left a customers house where it did it again after two days of it cooling just fine. After manually short cycling the compressor by engaging and disengaging the contractor, the same noise occurred. So I know the problem is short cycling. After verifying terminals and wire nuts were all secure, Safety switch cuts of 24v to R terminal, And verifying thermostat has a time delay. The only reason I could narrow down to cause the compressor to short cycle is a faulty pressure switch.
Sorry if this has already been asked but do these problem systems possibly have nest thermostats?I just left a customers house where it did it again after two days of it cooling just fine. After manually short cycling the compressor by engaging and disengaging the contractor, the same noise occurred. So I know the problem is short cycling. After verifying terminals and wire nuts were all secure, Safety switch cuts of 24v to R terminal, And verifying thermostat has a time delay. The only reason I could narrow down to cause the compressor to short cycle is a faulty pressure switch.