HVAC-Talk: Heating, Air & Refrigeration Discussion banner
1 - 10 of 10 Posts
The Wet Bulb temp, is a way to measure the amount of heat enerfy in the air.

Operating above or below those ratings, the systems performace, is not known.

Capacity may be greatly decreased.

Those ratings for that brand, give a pretty good leave way, on operating conditions.
 
Discussion starter · #5 ·
It will work as rated down to an indoor condition of 67°F DB, and 57°F WB.

At 61°F indooor DB temp, it will probably not remove enough moisture to keep the humidity below 55%.
I wonder if any of the mini-splits are particularly better at dehumidifying overnight? It would be much quieter than my portable dehumidifiers, so it's preferable to have the AC doing it.

So when you set it in "dry" mode in the evening, to keep on running slowly, whether there is anything different about the controls in different models to keep it running better for dehumidifying overnight?

I'm not sure at what point the compressor in "dry" mode stops running because the room temperature gets too low.

Laura
 
Laura,

Beenthere is correct that using the Dry function is rarely needed. I know you are concerned about the humidity as much, if not more, than the actual air temp. They do go hand in hand to a certain extent.

Since the system will have an inverter compressor, it will set the compressor speed so that it is cooling at the rate the space is gaining heat. This means the compressor will be running almost all of the time, and thus, providing de-humidification on an ongoing basis. Thus, sizing the system correctly will be important for it to function best.

Most mini-splits do not monitor the temp when in Dry mode. The way it de-humidifies in Dry mode is to slow the indoor fan to the lowest speed and then run the compressor for a few minutes at a time, cycling it on and off. It will continue to do that and if the space is not gaining heat as fast as the space is being cooled, then it will get over-cooled.

The best way to condition the space for comfortable humidity is to keep it conditioned on an ongoing basis. By keeping the space conditioned throughout the day it will help keep it conditioned through the night. This does assume the home is not like a piece of Swiss cheese and can keep the cool dry air in and the warm moist air out for some reasonable period of time.
 
Discussion starter · #8 ·
Few homes need to use the dry feature. It tends to over cool too much.
I do. I want it to keep on running slowly overnight, to dehumidify, even if it gets cold. Not to stop when it gets below a certain temp.

Is there a particular brand that's preferable for this? Or do they all run about the same way?

thanks
Laura
 
Discussion starter · #9 ·
Laura,
Since the system will have an inverter compressor, it will set the compressor speed so that it is cooling at the rate the space is gaining heat. This means the compressor will be running almost all of the time, and thus, providing de-humidification on an ongoing basis. Thus, sizing the system correctly will be important for it to function best.
Thanks, that is useful info. Because the contractors will assure me that I should have a largish system to avoid the possibility of not being cool enough. And that with an inverter compressor I shouldn't worry about oversizing it.

I got the roof ventilated and it made a drastic difference in how much it heats up during the day. So, I don't know how sizing can be exactly done. Because subtleties like how much air circulation there is in the roof wouldn't appear in a Manual J and they're very hard to quantify anyway.

Laura
 
Thanks, that is useful info. Because the contractors will assure me that I should have a largish system to avoid the possibility of not being cool enough. And that with an inverter compressor I shouldn't worry about oversizing it.

I got the roof ventilated and it made a drastic difference in how much it heats up during the day. So, I don't know how sizing can be exactly done. Because subtleties like how much air circulation there is in the roof wouldn't appear in a Manual J and they're very hard to quantify anyway.

Laura
There is a wider margin for over sizing without problem with an inverter system. But, the system can still be over sized to the point that it is not as effective as it could/should be. Plus, the cost of a larger system is higher.

Sizing the unit by calculating the heat gain/loss using Manual J is still the correct way of doing it. All the unique issues of your home can be factored when doing the calculation.
 
1 - 10 of 10 Posts