What is the best method and location to determine evaporator coil temperature?
Thanks for reply and I have enjoyed your many comments concerning humidity on this forum.Sounds like you should not change anything. I prefer using the suction pressure to determine the coil temperature. Go for a 45^F coil by converting the suction pressure to the boiling point of the specific refrigerant. The air temp off the coil will be 5-7^F warmer than the coil.
Hope this helps.
Regards Teddy Bear
Running longer with a cooler coil should remove more humidity. It is really critical that the coil temperature is at or below return air dew point so that the water is squeezed off as it circulates. Locking it in S1 until stat setpoint is exceeded might help.Thanks for reply and I have enjoyed your many comments concerning humidity on this forum.
I have no way to measure the suction pressure so I will assume the air temp off the coil, as you mention, will be 5-7^F warmer than the coil. This information is very useful.
Currently the compressor activates stage 2 (hi) when the discharge air temperature is above 57 degrees and then switches to stage 1 (lo of 70% capacity) when discharge air is below 57 degrees.
Above, I think, shortens cycle time. Would I be better off as far as humidity if I prevent stage 2 (hi) from activating for a longer period of time? Would this save electricity or be about the same? Colder coil and shorter cycle time or slightly warmer coil and longer cycle time?